Yes, I have been able to use the Minitor II, Minitor III and IV, Minitor V, and Minitor VI amplified chargers interchangeably over the years. The accessory connector pinout doesn't seem to have changed.

The alerting system I made uses pins 2, 3, 4, and 5. Pins 1 and 6 are not used in my system.
 

MTRescue740

New Member
Was anyone able to figure out how to get ithe amplified charger to reset automatically? For example, when our tones go off, the pager goes off twice within about 20-30 seconds depending on the dispatcher. From my testing, the lights only go off the first time and will not go off again unless the amplified charger is reset
 

shues

Lifetime VIP Supporter
Was anyone able to figure out how to get ithe amplified charger to reset automatically? For example, when our tones go off, the pager goes off twice within about 20-30 seconds depending on the dispatcher. From my testing, the lights only go off the first time and will not go off again unless the amplified charger is reset

You're probably experiencing this because pins 4 and 5 are connected. Try breaking that circuit.

Pins 4 and 5 of the accessory connector are used to select the time duration of the relay contact closure. If these two pins are NOT used (open circuit), the relay will remain energized for approximately 10 seconds after an alert is received. If pins 4 & 5 are SHORTED, the relay will remain energized until the 'RESET' button on the front of the charger/amplifier is depressed. Pressing the 'RESET' button causes the contacts to open and turns off the ALERT indicator."
 

Doyle257

Site Veteran
This is a goldmine for the system im installing in my home!
 

MTRescue740

New Member
You're probably experiencing this because pins 4 and 5 are connected. Try breaking that circuit.
I pulled the system out of service and I was using pin 4 (white cable) and the shield. The system works but has to be reset manually, do you know which pins i need to use?
 

shues

Lifetime VIP Supporter
With pins 4 and 5 connected, you're setting your relay to require manual reset. Disconnect pin 4 from pin 5 to set your relay for automatic reset.
 

MTRescue740

New Member
The relay we're talking about is internal to the amplified charger base.
I am not going to lie, I am kind of lost now, I'm probably over thinking about this. I am using the amplified charger to trip the Altronix 6062 board. I was originally using the white cable (pin 4) as the trip and the shield as the ground.

I need to figure out which pin to use instead of 4 for the automatic reset. We don't get a lot of calls so I can only verify it every so often, which is why I haven't figured it out yet through trial and error.

I can go over there and get a picture if that helps
 

shues

Lifetime VIP Supporter
Pins 2 and 3 correspond with the terminals of the dry contact relay inside of the amplified charger base. This relay is tiny. It can handle at most 750 milliamps while closed, it can switch at most 400 milliamps. It can take no more than 28 volts DC, and is rated at only 10 watts.

I use the dry contact relay inside of the amplified charger base and a very small wall-wart to trigger a solid state relay that does the heavy lifting. I have pins 4 and 5 shorted together so that the output stays active until the reset button is pressed.
 

tangelella

New Member
Question about this system. My department just installed speakers for audio and a bunch of horn/strobes hooked to an altronix 6062, powered by a minitor vi amplified charger. The problem we are having is that the horn strobes are so delayed on activating that they can only activate for 2 seconds before having to cut out for the dispatch. We get the beeps over the audio speakers for about 5 seconds before the horns activate. is there a way to change this so that the horns activate instantly upon tripping?
 

tangelella

New Member
so we had the company who installed the system here today and they think the delay is that the system needs to be 24v or the problem is in the horn strobes and may have to swap them out for different ones. Does that sound right?
 

MtnMan

Senior Member
so we had the company who installed the system here today and they think the delay is that the system needs to be 24v or the problem is in the horn strobes and may have to swap them out for different ones. Does that sound right?
Sounds like they have no clue.
 

Quentin

Senior Member

This is what I put together. This uses two-tone detect that sends a trigger to a MQTT broker then node-red gets the trigger. From node-red the possibilities are endless. I have it also turn on my bedroom/hallway/garage lights between dusk and dawn with a 2min timmer to turn off.

The sounds is coming over a Sonos speaker and using a Wemo switch a generic 12v 5a power supply.
 